Draft STANDARD SAVINGS ESTIMATION PROTOCOL FOR PUMP VFD Submitted to REGIONAL TECHNICAL FORUM Submitted by SBW CONSULTING, INC. 2820 Northup Way, Suite 230 Bellevue, WA 98004 January 28, 2011 Standard Savings Estimation Protocol - Fan VFD TABLE OF CONTENTS 1. PURPOSE............................................................................................................ 1 2. DEFINITION OF KEY TERMS ..................................................................................... 1 3. ELIGIBLE PROJECTS ............................................................................................... 1 4. REQUIRED KNOWLEDGE AND SKILLS OF PRACTITIONER ................................................... 1 5. REQUIRED COMMISSIONING .................................................................................... 2 6. DATA COLLECTION REQUIREMENTS ........................................................................... 2 6.1. Pump Motor Specifications................................................................................................ 2 6.2. Pump Operations ............................................................................................................... 2 6.3. Baseline Measurements .................................................................................................... 3 6.4. Post-Period Measurements ............................................................................................... 3 6.5. Typical Meterological Year (TMY) Weather Data .............................................................. 3 6.6. Inputs for Cost-Effectiveness Analysis ............................................................................... 3 7. PROVISIONAL DATA REQUIREMENTS ......................................................................... 4 8. SAVINGS ESTIMATION STEPS ................................................................................... 4 8.1. Prepare Trend Log Data ..................................................................................................... 4 8.2. Annualized Savings............................................................................................................. 5 8.3. Life Cycle Costs and Benefits ............................................................................................. 5 9. SAMPLING PROCEDURE .......................................................................................... 5 10. RELATIONSHIP TO OTHER PROTOCOLS AND GUIDELINES ............................................... 5 11. TYPICAL COST OF APPLYING THIS PROTOCOL ............................................................. 6 12. USER’S GUIDE TO PUMP VFD SAVINGS CALCULATOR .................................................. 6 SBW Consulting, Inc. i Standard Savings Estimation Protocol - Fan VFD 1. PURPOSE This protocol establishes a method by which annual electrical energy savings (kWh) can be estimated for a pump that has been upgraded by the addition of a Variable Frequency Drive (VFD). VFDs reduce electric use by adjusting the pump motor’s speed to match the required load. Many pumps do not need to run at full capacity all of the time, and VFDs are more efficient than other methods, such as throttling valves, at regulating flow rates. This protocol specifies minimum acceptable data collection requirements and the method by which these data are to be used in computing savings for Pump VFD projects. Savings are computed using the Excel workbook (to be developed) that accompanies this document to ensure standardized application of the savings estimation methods. 2. DEFINITION OF KEY TERMS Project. A project consists of one VFD installed to control a single pump. Modifications are made to valves as needed throughout the distribution system to allow for flow variation in the post period. Baseline. This modifier; as in baseline power refers to the period prior to the upgrade. Post. This modifier; as in post power trend log, refers to the period after the pump VFD upgrade is installed and fully commissioned. Commissioning. This is the process of testing and adjustment required to ensure that the pump VFD is operating according to its design intent. 3. ELIGIBLE PROJECTS The following criteria define eligible projects. Baseline flow must be constant. This excludes variable flow conditions such as pump cycling or twoway valves on equipment served by the pump. Systems where pump flow varies with production level are excluded. Pump must be directly driven by an electric motor. Diaphragm pumps driven by compressed air are not allowed. New construction projects are not eligible. The cost of implementing this protocol must not make the project economically unattractive. 4. REQUIRED KNOWLEDGE AND SKILLS OF PRACTITIONER The practitioner who has lead responsibility for applying this protocol must have a full understanding of the following: SBW Consulting, Inc. 1 Standard Savings Estimation Protocol - Fan VFD Appropriate safety procedures for work involving pumps and the measurement equipment required by this protocol This protocol and the accompanying savings calculator. The practitioner must also be able to successfully perform the following tasks: Identify, by inspection and discussion with facility staff that the baseline flow is constant. Identify the determinants of post period variations in flow: (1) outside air temperature or (2) facility operations schedule. Supervise a licensed electrician in installing sensors for true power measurements on the pump motor and VFD. Install and operate a true power logger and obtain necessary trend logs from facility control systems. 5. REQUIRED COMMISSIONING This protocol may only be used for pumps that pass the following commissioning tests: Review of installation documentation confirms that intended valve modifications have been made throughout the distribution system. Plot of VFD power during the post period confirms that the pump was responding to the control signal at least 90% of the trend log (see 6.4). VFD power should change in response to changes in facility operating modes and outside air temperature. 6. DATA COLLECTION REQUIREMENTS The following data must be collected and entered into the savings calculator. The minimum acceptable procedure for obtaining the data is specified. 6.1. Pump Motor Specifications Pump Motor HP. Obtained from the motor name plate. Full load pump kW (computed by the savings calculator) should not exceed 115% of pump motor nameplate HP times 0.746. 6.2. Pump Operations 2 Determinants of Pump Speed. Obtained from facility operator. There are two possible determinants: (1) outside air temperature or (2) facility operations schedule. In some cases, both the outside air temperature and facility operation schedule are determinants of pump speed. SBW Consulting, Inc. Standard Savings Estimation Protocol - Fan VFD Outside air temperature. The practitioner must determine how outside air temperatures (OAT) affect pump operation. One of three types of OAT driven applications are possible: (1) cooling driven (as in a chilled water pump), (2) heating driven (as in heating hot water pump), or (3) both heating and cooling. Facility Operations Schedule. Obtained from facility operator. Schedule may include daily, e.g. nighttime setback, or seasonal variations in operating modes. If the pump has different operation modes determined by the facility’s operations schedule, determine the periods for each mode defined by hour of day, day of week and season. Weather Station. If OAT is a significant determinant, identify the TMY (Typical Meteorological Year) weather station which is closest to the project site. 6.3. Baseline Measurements Pump Motor power. A one-time measurement of true RMS poly-phase power on the circuit powering the pump motor. 6.4. Post-Period Measurements Trend Log of VFD Power. A data logger is installed to measure 15-minute interval true RMS polyphase power on the circuit powering the VFD. If pump flow is determined by OAT, the period must representative of temperatures relevant to the pump application (heating, cooling or both). If pump flow is determined by facility operations schedule, the period must be representative of all important modes of operation. Trend Log of VFD Facility OAT. The facility’s control system is programmed to record OAT at 15minute intervals. This data must be collected for the same period as the VFD power trend log. This data is required only if pump flow is determined by OAT. If OAT is not available from the facility’s control system or appears unreliable, an OAT data recorder should be installed to create this trend log. 6.5. Typical Meterological Year (TMY) Weather Data TMY OAT. Typical Hourly OAT data for Pacific Northwest weather stations are contained in the savings calculator to be used in estimating annual savings. Data from the station selected in 6.2 will be used. 6.6. Inputs for Cost-Effectiveness Analysis The following data need to be gathered to support the cost/benefit analysis feature of the calculator. Project completion date. SBW Consulting, Inc. 3 Standard Savings Estimation Protocol - Fan VFD Measure cost. The initial cost of installing the new equipment, including all materials and labor costs. This is the full cost of the VFD installation. This value must be supported by invoices or other documentation. Sector. Possible values are Agricultural, Industrial, and Commercial. The following values are used in the cost-effectiveness calculation, but are pre-set in the calculator. Electric shape. The calculator assigns an appropriate electric shape based on fan operation data describe in section 6.2 and the profile of savings computed from the trend log data. Periodic costs or savings. Any non-annual periodic costs associated with the measure, and the associated time period. These are incremental costs of the efficient option over the costs of the baseline. For a pump VFD, the calculator restricts this value to be zero. O&M costs or savings. Annual O&M costs or savings associated with the measure. These are costs or savings which occur with the efficient option that would not occur with the baseline option, i.e. the costs associated with VFD maintenance. The calculator restricts this value to be zero. Non-energy benefits. Annual non-energy related costs or savings associated with the measure. The calculator restricts this value to be zero. Measure life. Number of years the measure is expected to be in effect. For a pump VFD, the calculator restricts this value to be 10 years. 7. PROVISIONAL DATA REQUIREMENTS During the period that the RTF classifies this protocol as Provisional, the following data requirements will be in force: Trend baseline motor power. A data logger is installed to measure 15-minute interval true RMS poly-phase power circuit powering the pump motor for a period of at least two weeks. This measurement is used to confirm baseline flow is constant. 8. SAVINGS ESTIMATION STEPS Savings are estimated using the savings calculator that accompanies this protocol (To be developed). Savings are estimated as follows. 8.1. Prepare Trend Log Data Data Synchronization. Start times for all trend log intervals are synchronized by moving each to the closest standard interval start times of 0, 15, 30 and 45 minutes after the start of each hour. Savings for Trended Period. For each interval, savings will be equal to baseline pump power minus the trend long value for post VFD power. 4 SBW Consulting, Inc. Standard Savings Estimation Protocol - Fan VFD 8.2. Annualized Savings Average Savings by Trend Log Bin. For each operating mode, average kW usage by two degree temperature bins, for all trend log intervals during operating hours, as defined by facility operations schedules (Section 6.2). Average Savings by TMY Bin. For each operating mode, TMY bin average savings equal trend log average bin savings for each matching bin. Extrapolate average savings for TMY bins that do not have trend log data. For heating savings, values are extrapolated by a best fit equation to the trend log bins. Negative values will likely occur at temperatures greater than about 60F and should be set to zero. For cooling savings, values are extrapolated by a best fit equation to the trend log bins. Negative values will likely occur at temperatures less than about 60F and should be set to zero. No bin value is allowed to exceed the rated pump motor kW. Annual Savings. Sum the kWh values across all bins. 8.3. Life Cycle Costs and Benefits The calculator contains a model called ProCost which computes life cycle costs and benefits. Inputs to the model include the estimates of first-year savings and the cost-effectiveness input data described in section 6. ProCost computes life cycle costs and benefits from the economic perspectives of the end user, utility, and region. The calculator can be used to review these results. 9. SAMPLING PROCEDURE No sampling is permitted by this protocol. Data collection and savings estimation is required for each upgraded pump regardless of the number of such units that may be upgraded at a facility. 10. RELATIONSHIP TO OTHER PROTOCOLS AND GUIDELINES The relationship between this protocol and other relevant protocols and guidelines is as follows: International Performance Measurement and Verification Protocol – 2007 (IPMVP), Efficiency Valuation Organization. This protocol is consistent with Option B - Retrofit Isolation: All Parameter Measurement described in the IPMVP, as power and other key parameters are measured (pump motor power, VFD %speed and OAT) in both the baseline and as-built cases. M&V Guidelines: Measurement and Verification for Federal Energy Projects Version 3.0, U.S. Department of Energy Federal Energy Management Program. The relevant part of this guideline is Section 11.4 Variable Speed Motors. This guideline requires both baseline and post measurements, which is consistent with this protocol. Sampling Reference Guide, BPA. It is unlikely that more than 20 pump units would be upgraded as part of any one project. It is difficult to obtain reliable sample estimates from populations this small, SBW Consulting, Inc. 5 Standard Savings Estimation Protocol - Fan VFD especially given the likely variation in savings between units. Therefore no sampling is allowed. This is consistent with the BPA guide. Regression Reference Guide, BPA. This protocol uses regression techniques to extrapolate savings to temperatures beyond those observed in the trend logging period (for pump units whose speed is primarily determined by OAT). The application of these regression techniques is consistent with the BPA guide. 11. TYPICAL COST OF APPLYING THIS PROTOCOL Shown below is an estimate of typical cost of applying this protocol for a single pump unit. Projects that involve more than one pump unit at the same facility are likely to see lower cost per unit. Expense for alternative measurements, allowed by this protocol, are not included in this estimate of typical cost. Item Quantity $ / Hour Rental Total Cost Equipment Power Meter 1 100 100 Power Logger 1 400 400 Labor Practitioner Travel 4 110 440 Scheduling 2 110 220 Facility Operator Interview 1 110 110 VFD Inspection 1 110 110 Electrical Measurements 1 110 110 Install/Remove Power Logger 4 110 440 Savings Estimate 4 110 440 Travel 4 90 360 Electrical Measurements 2 90 180 2 150 300 Electrician Controls Specialist Setup and Export Trend Logs Total $3,210 12. USER’S GUIDE TO PUMP VFD SAVINGS CALCULATOR [To be developed once this protocol is finalized and savings calculator is developed. This Guide and the Calculator are outside the scope of SBW’s current contract.] 6 SBW Consulting, Inc.