Conservation Voltage Reduction (CVR) Voltage Optimization (VO) Josh Rushton Regional Technical Forum July 21, 2015 2 Objective Today, we’re seeking RTF decisions on two standard protocols: • Automated CVR: Recommend deactivation. – Intent is only to move to Custom Protocols – Protocol’s method is still a reasonable approach – Still a lot of CVR savings out there • Simplified VO: Recommend approval. – Proven category, active status. – Proposal includes major protocol changes 3 Outline • Background • Simplified VO – The big shift – Reliability – Decision • Automated CVR 4 Background 5 -- Background What are these measures about? Basic idea: 126 Some things use less energy at lower voltages 124 Voltage 122 120 118 Complication 1: 116 Average ΔV can be hard to estimate 114 Complication 2: ΔV 112 0 2 4 8 Miles from substation Savings factors (%ΔKWh per %ΔV) depend on end-use mix. • • 6 (PNNL, 2010) gives some lab results; (NEEA, 2008) reflects residential mix circa 2006. Artist’s rendering (fake data) 6 -- Background Two Standard Protocols Automated CVR Protocol #1: Collect 90 days of alternating dayon/day-off data, use to estimate feeder-specific savings factors • • Early version approved by RTF in 2004 Major revision November, 2011 (latest draft dated May 15, 2012) – Stalled out in subcommittee – Main sticking point was proposed eligibility requirements %ΔkWh %ΔV Simplified VO Protocol: “Canned” savings factors derived from NEEA’s DEI research (NEEA, 2008) • • Early version approved by RTF May, 2010, good background info in April, 2010 Revised version brought to RTF in November, 2012 – RTF sent back to subcommittee for further discussion – Subcommittee took a step back to consider a change of course Both protocols stalled out at end of 2012 • Both currently Under Review. 7 - Background Recent RTF Direction • RTF (January, 2015): Find out what it would take to “dress up” the protocols – Clarify terms like mostly residential, review treatment of persistence, … – Check whether eligibility can be expanded • Subcommittee: CAT should compare requirements to DEI study/data • Result: No clear answers without major effort; probably none with major effort • RTF (January, 2015): Are RTF standard protocols really a good fit for these measures? – RTF Standard Protocols seem too narrow – Maybe some kind of “custom guidance” would be better – Subcommittee (May, 2015): Very limited discussion of this issue 8 Simplified VO Protocol 9 – Simplified VO Measure Overview • Measure Name: Voltage Optimization • Method: Standard Protocol • Category: Proven • Current Status: Under review • Proposed Status: Active • Proposed Sunset Date: July, 2020 • Highlighted areas: Eligibility, reliability 10 – Simplified VO Two Standard Protocols Automated CVR Protocol #1: Collect 90 days of alternating dayon/day-off data, use to estimate feeder-specific savings factors • • Early version approved by RTF in 2004 Major revision November, 2011 (latest draft dated May 15, 2012) – Stalled out in subcommittee – Main sticking point was proposed eligibility requirements Simplified VO Protocol: “Canned” VO savings factors derived from NEEA’s DEI research (NEEA, 2008) • • Early version approved by RTF May, 2010, good background info in April, 2010 Revised version brought to RTF in November, 2012 – RTF sent back to subcommittee for further discussion – Subcommittee took a step back to consider a change of course Both protocols stalled out at end of 2012 • • • Both currently Under Review. Recommend deactivating Automated CVR Protocol #1 Recommend approving modified version of Simplified VO Protocol 11 – Simplified VO The “canned” VO factors • VO factors quantify %ΔkWh per %ΔV • Values in VO factor table based on NEEA Load Research Project – Vary by climate, saturation of AC and ER heat – Only counts end-user energy savings (distribution losses calculated separately) – Reflect residential end-use mix • Tables need periodic review/update to reflect changes in end-use stocks • May be possible to expand tables to include values for VO factor more commercial loads 12 – Simplified VO Motivation Why build an RTF protocol around the VO factor tables? • VO factor tables have potential to simplify savings estimates for a lot of feeders • An RTF protocol has several functions – Describing how to get reliable estimates from simplified methods – Maintaining reliability via sunset check-ins – Making conservation credits more predictable 13 – Simplified VO The tricky part VO factor (%ΔkWh / %ΔV) only useful if you can estimate ΔV • Why? Savings estimated as ΔkWh = kWhAnnual * VOf * %ΔV • What? ΔV target is average annual change in voltage experienced by end users • How? That’s the tricky part. – Easy to estimate ΔV for very linear systems • Performance thresholds increase linearity but restrict eligibility • See Additional Slides for details – Voltage usually not very linear in the wild – Are reliable ΔV estimates ever possible without meeting all thresholds? (Answer: Probably sometimes) 14 – Simplified VO Proposed approach • Describe the circumstances and method where we know savings is reliable • Point out some things you need to be careful about when you deviate from that method or those circumstances • This is a new approach to RTF Standard Protocols. 15 – Simplified VO How the proposed protocol works • Proposed Protocol describes Benchmark Method, same as sole Savings Method in previous protocol drafts. – Savings method (with formulas that assume linearity) – Performance thresholds (which support linearity and measure persistence) – Data collection (what’s needed for savings method inputs and reliability checks) – Details in Additional Slides • Proposal allows other approaches (besides Benchmark Method) but does not specify alternatives – Totally different, unforeseen, approaches – Minor tweaks (may alter savings method, performance thresholds, data collection, or any combination) 16 – Simplified VO Proposed Reliability Framework • Basic Eligibility Requirement: “The practitioner can reliably estimate the average annual change in voltage that is experienced by end-users as a result of the measure” • Reliability Standard: “…reliability similar to the Benchmark Method” • Validity Threats: “At a minimum, protocol documentation must demonstrate that the final calculations address” threats related to four issues: Extrapolation, Annualization, Baseline, Persistence – Protocol notes how performance thresholds address threats in Benchmark Method – Protocol does not specify what it means to address the threats in general • Language similar to above used in both Eligibility and Delivery Verification sections • Intent: Describe circumstances where RTF “certifies” reliability. Leave grey areas of reliability to regulators, evaluators, and utilities, but with “some lines drawn on the playing field” 17 – Simplified VO Validity Threat: Extrapolation “Is the ΔV estimate based on a reliable approach to extrapolating data collected at the selected metering locations (e.g., source and EOL) to customers along the feeder? “In the benchmark method, this extrapolation is based on a linear model of voltage decay along the length of each feeder, and the performance thresholds support this linear assumption.” 18 – Simplified VO Other Validity Threats • • • • Annualization Baseline Persistence See Additional Slides 19 – Simplified VO Minor Changes • Clear statement of “right-on-average” reliability standard • “Mostly residential” requirement given specific definition (at least 80% of feeder load due to residential end-users, the rest light commercial) • Moved four-step integrated planning process to Appendix • Removed delivery verification items that only related to the planning process (rather than reliability of savings) • Editorial stuff 20 – Simplified VO Staff/CAT Recommendation Recommend approving Simplified VO Protocol with proposed modifications • Status: Active • Category: Proven • Sunset date: July 31, 2020 21 – Simplified VO Proposed Motions “I, _________, move that the RTF approves the Standard Protocol for Voltage Optimization as presented (active status, proven category, sunset date of July 31, 2020)” 22 Automated CVR Protocol #1 23 – Automated CVR Two Standard Protocols Automated CVR Protocol #1: Collect 90 days of alternating dayon/day-off data, use to estimate feeder-specific savings factors • • Early version approved by RTF in 2004 Major revision November, 2011 (latest draft dated May 15, 2012) – Stalled out in subcommittee – Main sticking point was proposed eligibility requirements Simplified VO Protocol: “Canned” savings factors derived from NEEA’s DEI research (NEEA, 2008) • • Early version approved by RTF May 4, 2010 Revised version brought to RTF in November, 2012 – RTF sent back to subcommittee for further discussion – Subcommittee took a step back to consider a change of course Both protocols stalled out at end of 2012 • • • Both currently Under Review. Recommend deactivating Automated CVR Protocol #1 Recommend approving modified version of Simplified VO Protocol 24 – Automated CVR Savings method summary • Data collection: Minimum of 90 days, raise and lower control-zone voltage to get day-on/day-off CVR operation cycles. • Savings factors: Primary data used to estimate feeder-specific savings factor (%ΔKWh/%ΔV) for each application – Factors capture savings on both sides of meter – Protocol directly measures switchable savings (models used capture other savings components) • Energy savings: Savings estimated as product of savings factor, annualized average ΔV, annual kWh (based on historical data). 25 – Automated CVR Reasons to deactivate • Method (day-on/day-off) is a version of best-practice – Has traction (people reference it, use as benchmark) – Little or no simplification over custom alternatives – Primary value is consistency of estimation method • Practitioners want more flexibility – – – – Performance thresholds are controversial Minor tweaks (e.g., how to normalize for weather or weekends) Very different methods (e.g., all-year-on study, w/ comparison feeders) Existence of proven RTF Protocol not supposed to obstruct alternative methods (but some say it does) • Staff/CAT/Subcommittee resources needed to land the protocol – – – – Find a path through (or around) performance thresholds Incorporate model improvements / tweaks Would push back other measures (for what pay-off?) Might fail to land anyway 26 – Automated CVR Effect of deactivation • Eligible projects will have to go Custom (most already end up there) • Day-on/day-off method will have no home within a proven RTF document – Doesn’t mean method isn’t reliable – Document will remain on RTF website – Practitioners/regulators may still agree to use the approach when helpful • Reserve RTF Staff/CAT/Subcommittee resources for other tasks 27 Proposed Motion “I, _________, move that the RTF deactivates the Automated CVR Standard Protocol #1 because the protocol’s value to stakeholders is not sufficient to justify the RTF resources needed to prove out the protocol. – This decision does not imply that the protocol’s method is unreliable; – This decision does not imply diminished savings potential for eligible measures.” 28 Additional Slides 29 – Additional Slides Simplified VO: Baseline Notes From the proposed protocol: “Baseline. A term from the RTF Guidelines. The Baseline is the inefficient-case performance level referenced in savings calculations. Voltage optimization uses a pre-conditions baseline, which means that savings estimates should try to capture the difference in energy consumption between the pre-existing system and the efficient-case system, except when the pre-existing system includes obsolete equipment (in which case, the Baseline is the hypothetical system that would result if essential improvements were made to the pre-existing system). • “Some measure applications include or coincide with physical system improvements that are designed to drive deeper savings or improve system reliability. These measures can also lead to more predictable system performance, which may improve reliability of the average annual voltage estimates. In such cases, it may be possible to improve savings reliability by estimating Baseline performance using meter data collected after physical improvements are completed, but using operational settings that emulate average voltage conditions of the PreExisting System. The Benchmark Method takes this approach.” • “This protocol does not specify what constitutes obsolete equipment in a distribution system. A generic test is that equipment is obsolete if near-term improvements would be inevitable, even if the energy-efficiency measure was not being implemented.” 30 – Simplified VO Simplified VO: Validity Threats (1) Annualization “Is the ΔV estimate based on a reliable approach to annualizing data collected during the metering period? “In the benchmark method, the meter-period voltage estimates are scaled up or down in proportion to the ratio (average annual demand)/(average meter-period demand). This kind of scaling assumes that voltage normally rises and falls roughly in proportion to demand; this assumption is supported by the performance thresholds.” 31 – Simplified VO Simplified VO: Validity Threats (2) Baseline “Does the ΔV estimate reflect the correct baseline? See [Baseline Notes, above]. “If the VCZ includes obsolete equipment prior to the Voltage Optimization measure, then the correct baseline is not the same as the base-case system. Instead, it is the system that would result if the obsolete equipment were replaced with components that would be typical choices in the current market.” 32 – Simplified VO Simplified VO: Validity Threats (3) Persistence “Can reasonable assurance be provided that the efficient-case voltage settings will persist? In all applications of this protocol, delivery verification requires that a 3-year persistence plan must be documented to ensure that efficient system operation habits become well-established. However, a persistence plan will not be followed if customers experience adverse low-voltage events during some portions of the year.” “In the benchmark method, the performance thresholds ensure predictable and reliable system performance throughout the year so that efficient-case operations can be designed to reliably avoid low-voltage events.” 33 – Additional Slides Simplified VO: Benchmark Method Performance Thresholds (1) • Power factor (3-phase total, at source): – Minimum (hourly) greater than 0.96 – Average (for week) greater than 0.98 • Phase load balance (3-phase lines, at source) – Per-unit unbalance < 0.15 – Neutral < 40 amps • Max-adjusted voltage drop (3-phase mean) – Max-adjusted drop is mean meter-period drop, times (annual peak kW) / (mean meter-period kW) – Primary max-adjusted drop < 3.3% – Secondary max-adjusted drop < 4.0% 34 – Additional Slides Simplified VO: Benchmark Method Performance Thresholds (2) • Variation between feeder max voltage drops – Compare feeders within substation control zone – Must not differ by more than 2 Volts (on 120 V base) • Primary line minimum hourly voltage – Measured near expected low voltage point – At least 114 V + (1/2) Voltage regulation bandwidth + secondary max allowed voltage drop • Primary line maximum hourly voltage – Measured near expected high voltage point – Less than 126 V - (1/2) Voltage regulation bandwidth • Conductor loading – Source hourly loading (amps) less than design normal spec 35 – Additional Slides Simplified VO: Benchmark Method Savings Method Step 1. (Identify Savings Factor) Look up VOf (%ΔkWh / %ΔV) in table • Values vary by climate, saturation of AC and ER heat • Remember: VOf only counts end-user energy savings (distribution losses calculated separately) Step 2. (Estimate ΔV) See next slide. Step 3. (Estimate Energy Savings) ΔkWh (savings) = kWhANNUAL * VOf * %ΔV • kWhANNUAL based on historical data • ΔV is estimated average voltage difference between CVR-on and CVR-off cases 36 – Additional Slides Simplified VO: Benchmark Method Formula for Estimating ΔV For fixed voltage reduction, VO Protocol estimates average voltage as follows, pre and post, and takes the difference: 1 π·ππππ’ππ π = ππππ‘ − ∗ π΄π£π πππ’π‘,π − ππΈππΏ,π ∗ 2 π·πππ‘ππ ππππ‘ = Regulator set point voltage setting πππ’π‘, π = Hour-i metered regulator output voltage on 120 V base ππΈππΏ, π = Hour-i metered EOL primary voltage on 120 V base π·ππππ’ππ = Average annual kW demand (from measured historical data) π·πππ‘ππ = Average kW demand, metered at source (Formula for line drop compensation and automated voltage feedback control adds correction for volt rise.) 37 – Additional Slides Some Recent DE Activity • NEEA DEI Project Final Report (NEEA, 2008) – Load Research Project (2005-2007) – Pilot Demonstration Project (c. 2005-2007) • • • • • • • • • • Distribution Efficiency Guidebook (NEEA, 2008) Long-Term Monitoring and Tracking DE (NEEA, 2014) Energy Smart Utility Efficiency (ESUE) Program (BPA, ongoing) PacifiCorp DE Pilot Study IEEE P1885. Guide for Assessing, Measuring and Verifying Volt-Var control Optimization on Distribution Systems (Draft - Approval expected 2017) Puget Sound Energy currently implementing VO Avista CVR Program Impact Evaluation (Avista, 2014) Evaluation of CVR on a National Level (PNNL, 2010) M&V research by PNNL and WSU researchers (2014) Green Circuits DE Case Studies (EPRI, 2011)